If you're getting 400+psi on the high side, there ain't nuthin' wrong with the valves in your compressor! Way too many compressors are replaced when there is nothing wrong with them. You can do this and replace some other stuff, too, and it'll probably be fine, but do you want to know what is really going on?
Clogged air passages on the condenser will make head pressure rise slowly. Same with non-functional fans.
A plugged orifice WILL cause the high side pressure to rise rapidly. And while , in theory, the suction side should go to vacuum, everyone seems to be forgetting that there is usually about 0.5 lbs of excess refrigerant in liquid form held in the accumulator. That liquid evaporates and keeps the low side pressure up, even though there is little to no flow returning.
Based on your description, the clutch is being disengaged due to the high pressure cut-off switch being triggered long before that excess charge is used up.
Evacuate (using proper reclamation equipment, please), and pull the orifice before spending lots of cash. The big concern is, what has plugged the orifice? There shouldn't be any debris, but if there is, it is likely that the compressor is goin' south due to wear/lack of proper oil circulation. Dark sludge is commonly observes when aluminum particles start mixing with the PAG oil used with R134a.
I'll bet that is what you'll find. If so, you'll need to flush the system to remove debris/sludge form the lines and heat exchangers. You may want to replace the accumulator because after 17+ years, the dessicant is probably used up. The desiccant absorbs moisture that, try as you might, you cannot evacuate.
Hope this helps.
Tedster